My boiler drops in pressure after every time it is in use.

 

I'm constantly having to top it up and i've noticed that water is coming out of the pipe to the exterior of my house.

 

Any ideas what the problem might be and how much it could be to fix.

 

 

Any help appreciated

 

 

Thanks

Edited by nikki-red
Link to comment
Share on other sites

Maybe the filling loop is bypassing. Easy way to check is to fill the system to 1.5 bar and then disconnect it. If you not happy to do this then fill to 1.5 bar but DONT use either hot water or heating for 6-12 hours. If you see the pressure valve rising then filling loop is the culprit.

 

HOWEVER, more than likely the expansion vessel has either lost pressure or the expansion pipe is blocked. This causes the pressure to rise (when the heating is on) to above 2.5bar and the safety PRV kicks in - hence noticing water outside. You will also need the PRV replacing

Link to comment
Share on other sites

Maybe the filling loop is bypassing. Easy way to check is to fill the system to 1.5 bar and then disconnect it. If you not happy to do this then fill to 1.5 bar but DONT use either hot water or heating for 6-12 hours. If you see the pressure valve rising then filling loop is the culprit.

 

HOWEVER, more than likely the expansion vessel has either lost pressure or the expansion pipe is blocked. This causes the pressure to rise (when the heating is on) to above 2.5bar and the safety PRV kicks in - hence noticing water outside. You will also need the PRV replacing

 

 

 

This sounds like the problem. How much is that to be fixed approximately

Link to comment
Share on other sites

[/u][/b]

 

This sounds like the problem. How much is that to be fixed approximately

 

Need to know make and model of the boiler first.

 

On some boilers you cant get to the expansion vessel (unless you remove the boiler from the wall). Therefore you 'tie' a new vessel into the existing system. Also gotta drain down. Again some boilers have quality isolation valves on the flow/return AND a drain off internally which makes for a quicker job. Unfortunatley most do not :rolleyes:

 

You also need a new 3bar PRV fitting as the old one will continue to leak.